- #21 [Thanatos], 20-10-16 23:25謝謝師兄指教
- #22 [bankguy], 20-10-16 23:37[#20] 咁即係賣爐間嘢好有問題。安裝上關鍵問題完全唔識。
- #23 [Ming Sir], 20-10-16 23:50死,唔係好 get 到添!?
我廚房係搵煤氣公司做(焗爐都幫趁佢),佢會劃好晒,改喉(指水喉,煤氣喉梗係煤氣公司自己改啦),去水丶電位等嘅圖,自己搵師傅或幫趁佢再判俾人做都得,咁我有裝修師傅梗係叫佢順便做埋啦,電焗爐位附近有個普通13A插頭位,我咪問下我裝修師傅用依個插頭位俾電焗爐(built-in果種)得唔得呢?於是衍生#20的對話!
最後,我當然有拉條獨立嘅32A俾佢啦!
最後修改時間: 2020-10-17 00:03:00 -
- #24 [winning7], 20-10-16 23:57如果唔拉好線焗爐師傅會唔肯裝。另外,裝修師傅亦唔會幫你裝 >>
佢地要承擔責任架....見倒條線唔夠A 都同你裝落去....同裝電熱水爐一樣
電焗爐位附近有個普通13A插頭位,我咪問用依個插頭位俾電焗爐(built-in果種)得唔得?>>
啱丫...佢嚴重提醒好正確....應該咁做
不過最近見有D裝修判頭.....其下有些分比大陸佬深圳黎做....大陸佬乜都話得....大家執生
焗爐我是外置, 所以也不貪心, 買個 10-11A....夠焗倒隻雞就算
最後修改時間: 2020-10-17 00:05:22 - #25 [bankguy], 20-10-17 00:18[#24] 焗爐唔係貴,係廚房空間貴。
- #26 [呀金], 20-10-17 00:20焗爐大部份時間係空置,唔抵!
kakaka~~~ - #27 [0925], 20-10-17 01:00如果電箱有空位裝一個獨立 30A mcb ,拉條30A 線用返原來的入牆喉和 13A 蘇底位換裝1個cooker switch。
不過如果住大廈個總 fuse 大掣得 ~63A,屋企又多冷氣機和大耗電量電器,個焗爐用細啲功率就安全啲。 - #28 [alexanderkoo], 20-10-17 09:23For induction cooker, not oven, 2.8 kW max. for supply by 13 A socket. In fact, should allow 20% safety margin.
There is twin unit for cooker unit and 13A socket in UK, not for sales in HK. Got one for my 2 nos.induction units. Must be protected by rcd and total loading not exceeding 30A MCB. New concealed cable, diy.
最後修改時間: 2020-10-17 09:27:58 - #29 [tomatonfc], 20-10-17 09:25氣炸鍋工能差唔多
- #30 [ich], 20-10-17 10:21#29
我屋企有焗爐、光波爐、朋友留低的菲利蒲氣炸煱.焗爐及光波爐常用.氣炸煱一次都未用過.焗爐及光波爐各有長處.
新式的所謂air fryer 四四方方,根本係一個細fan-forced oven. 發明Air fryer 及氣炸煱兩個 terms的marketing team真係勁. - #31 [skyliner], 20-10-17 11:00發明Air fryer 及氣炸煱兩個 terms的marketing team真係勁. x2
同三叔發眀LED電視,應該一齊攞諾貝爾...
文學獎
家下街市凍肉鋪都改名叫氣炸食品專門店。 - #32 [Ivansum], 20-10-17 11:14你直接叫電燈師父放條2.5行明線,加個20A燈曲(用靚D牌子,如mk)我自己就用30A(貴D),如電制箱夠位就比條獨立20A mcb落去最好,你同師父講就知点做架啦
- #33 [alexanderkoo], 20-10-17 15:01Concealed cabling can have practical difficulties, need to flip down the whole MCB board to expose the connection box underneath, trace the routing, conduit is usually very congested. Surface wiring is easier to work with but bad cosmetics.
I intended to have half way concealed but after flipping down the MCB board, I could draw wire from the kitchen hood socket to the board via the lampholder box at ceiling and lighting switch. - #34 [smallcircleson], 20-10-17 17:25
Code of Practice for the Electricity (Wiring) Regulations
https://www.emsd.gov.hk/filemanager/en/content_443/COP_E_2003.pdf
Code 26 REQUIREMENTS FOR SPECIFIC INSTALLATIONS AND EQUIPMENT (page 161)
26A Domestic Installation and Appliance
(1) Supply connection to domestic appliance
(a) For a single phase domestic appliance having a current rating
exceeding 13A to be used in an installation where only 5A and/or
13A socket outlets are provided, or a domestic appliance having a
current rating exceeding 15A to be used in an installation where only
5A and/or 15A socket outlets are provided, it should be connected
permanently (i.e. not through a plug socket) to a separate radial final
circuit and should be controlled by a double-pole switch in a readily
accessible position near the appliance.
(b) For supplying a single phase domestic appliance having a current
rating not exceeding 13A, the use of a radial or ring final circuit
using 13A socket outlets is acceptable.
(c) For supplying a single phase domestic appliance having a current
rating not exceeding 5A or 15A, the use of a radial final circuit using
5A or 15A socket outlet respectively, is acceptable.
(d) Adequate number of socket outlets for supply connections to
domestic appliances is to be provided for each individual household.
Table 26(1) recommends the acceptable minimum number of socket
outlets provided in various locations to afford the lowest quality of
service.
(2) Electrical equipment in kitchens
(a) For a circuit arrangement using 13A socket outlets to Code 6E,
separate circuits should be used for supply to electrical equipment in
kitchen other than luminaires.
(b) Every cooking appliance having more than one boiling or cooking
surfaces and with a total current rating exceeding 15A should be fed
from an exclusive radial final circuit and controlled by a double-pole
switch separate from the appliance and placed within 2 metres of the
appliance.
(c) Where two fixed or stationary cooking appliances are installed in one
room of household premises, one switch may be used to control both
appliances provided that neither appliance is placed more than 2
metres from the controlling switch.
(d) The switch for the cooking appliance of subparagraphs (b) and (c)
should be so positioned that the user does not have to lean across the
appliance in order to operate it. - #35 [0925], 20-10-17 17:34
- #36 [Mercury2015], 20-10-17 17:38(a) For a single phase domestic appliance having a current rating
exceeding 13A to be used in an installation where only 5A and/or
13A socket outlets are provided, or a domestic appliance having a
current rating exceeding 15A to be used in an installation where only
5A and/or 15A socket outlets are provided, it should be connected
permanently (i.e. not through a plug socket) to a separate radial final
circuit and should be controlled by a double-pole switch in a readily
accessible position near the appliance.
我想這個是理所當然的,即使13A入牆插坐裡面用了很粗能過30A的連接電線到能提供30A的電原, 13A入牆插坐本身的規格就不能插超過13A的電器, 否則13A入牆插坐本身會高温發熱燒毀.
最後修改時間: 2020-10-17 17:44:48 - #37 [felix], 20-10-17 17:40其實成個廳or房的插蘇加埋是13A
- #38 [olivea88], 20-10-17 17:43felix... 我苯唔同意....
- #39 [smallcircleson], 20-10-17 17:47
Best thing to do is to take a peek at the distribution panel (box) and identify the circuit breaker corresponding to the sockets (#1).
The current rating of the circuit breaker and the gauge of the wire limit the maximum current delivered to the sockets (#1).
You may be able to just change the circuit breaker to one with a higher current rating and heavier gauge wires which can be shuffled down the (original) conduit without having to install a separate external or internal 入牆 20/30A line, which inflicts substantial financial damage.
A double-pole.switch separate from the appliance placed within 2 metres of the appliance is mandatory.
最後修改時間: 2020-10-17 17:49:33 - #40 [alexanderkoo], 20-10-17 18:17#37, not necessarily true. Can be max. of 20 or 30A, depending on the rating of the MCB for the circuit. General rule of thumb without knowing the actual appliance in design stage, 5A/socket. 6 sockets for a 30 A MCB.